1756-IR12 unresponsive to RTD or resistor
chavak
Jul 2002
750
We had a new installation with Control Logix L81 which uses 2 of the 1756-IR12. Using Studio 5K Ver.30
We are facing no readings at the terminal of both the cards. It is connected with 100 Ohm PT385 RTD's [2 wire]. There is no fault displayed at the card, but the channels report a fault, with the underrange triggered true as well. The data is showing -200 Deg C, which is the lowest of the cards range. I think the card is not getting the field device into it. Tried with terminal B and C of each channel, link with and without a jumper as well, no difference
Contacted the Rockwell Tech connect as well as the local tech support, the problem still persists. Tech support advice to connect a 100 ohm resistor and see it reads 0 Deg C, tried that, but no response as well. Now the local tech support had bought back one of the card to their lab for testing. Anyway I have put up an order for a new card, as the project can't wait.
I noticed there are a 2 rows of 7 pin pairs on the card's PCB [as in the image below], which do not have any jumpers on it, can anyone please help to verify, is it suppose to have a jumper on it or left it open. Or any other advice for me to solve this issue.
Thank You
Best Regards
The spare card I ordered arrived, tested - working fine, without any change in connection or configuration.
So it was a pair of bad cards, my luck * 2
So, the pins I doubted do not need any jumpers on it. Nothing to do with that.
Regards
We ordered that same module for a project.
I'm preparing my remap section, so I was wondering.
Ch[x].Data
REAL Indicates channel data in ohms or Temperature.
Any positive or negative value. Determined by how you set the scaling parameters on the
channel.
So, will I be reading ohms or temperature? I cannot find a place where I can do the switch in the config, so I'm expecting temperature.
Since it's a REAL, Ch[x].Data should be the exact value in temperature right out from the box?
Hi all I have a ControlLogix 1756-L71SP that i want to use for general PLC applications, not safety. I am running Studio5000 v33, i can't...
84
404
Hi, I have two quick questions: 1- Could I use 1756-IA16/A with TTL inputs? Sourcing (PNP)? Sinking (NPN)? Either one? 2- What does /A in the part...
183
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
157
Hi, Is it possible to for an RIO with Flex 5000 series module, e.g. 5094-AEN2TR, to communicate with an 1756-L72E processor.
103