87hz Method with Powerflex 525

Jackllx

Lifetime Supporting Member
Join Date
Feb 2021
Location
UK
Posts
46
Hi,


I have a 2.2kw drive, this is a lift application and the manufacturer says to use the 87hz method. In theory I understand this but in practicality with a powerflex 525 i am unsure how to achieve this.


I have tried setting my motor data @ 50hz and 87hz, with my min freq at 0 and my max freq at 87hz.


I have increased the FLC of the motor and the OL current to suit it.


The drive is wired in delta and set up on a 3ph inverter with 400v.


I run the drive but it sounds really bad and then stalls.


Is there something I am missing here? Any help appreciated thanks
 
Are you using the low voltage Delta motor current in the PF525?

We have quite a few PF525's with Delta wired motors running without a problem. (except when some rewired the motor in Star and left the delta current settings in the PF525)
 
Last edited:
What values did you use for motor nameplate frequency and voltage?

Keith


Hi.

Motor Nameplate:
50hz
220-230/380/400
2.2kw
FLC @ 220v Delta = 8.4a
FLC @ 400v Star = 4.85a
RPM: 1450



Motor is wired in DELTA.



P525 - 5.5k2/ 3 phase

SVC Mode
Max Voltage: 400v
Motor NP Volts: 400v
Motor NP Hertz: 87hz
Motor OL Current: 16a
Motor FLA: 8.4a
Poles: 4
RPM: 1450 - I was unsure if to increase this to match 87hz

Power: 2.2kw



I have my max freq @ 87hz too.


I can get the drive to run now but it doesn't seem like its constant torque, do any of my settings look wrong?
 
Are you using the low voltage Delta motor current in the PF525?

We have quite a few PF525's with Delta wired motors running without a problem. (except when some rewired the motor in Star and left the delta current settings in the PF525)


Yes I am, but then the OL current is to be increased by a factor of 1.732 (root 3 squared)
 

Similar Topics

My boss has an idea: We have a project with 2 drives en 2 motors. 2 MM440's from Siemens. He tells me to connect the Motors in Triangle... The...
Replies
52
Views
17,962
sir, while running program in codsys an error occur 'C0138: No matching 'FB_Init' method found for instantiation of FbPowerPlantControl.' how to...
Replies
1
Views
83
Hi Guys, During PID Tuning by Ziegler Nichols Closed-loop method, In TIA Portal there is a Trend Tool used to determine Ultimate Period; marking...
Replies
9
Views
1,879
I'm using ftview 13 with rslogix v35. I want to use a button to reset all alarms coming from process CPU L83-EP. I tried using invoke method to...
Replies
10
Views
1,878
Good morning! I am looking for a clever method to determine the number of occurrences in a series using ladder logic. What I need to determine is...
Replies
6
Views
1,264
Back
Top Bottom