Alignment and FCS Error in compact logix

ravisk2411

Member
Join Date
Mar 2012
Location
Nashik
Posts
3
Hi friends,

Can any one help me with this
I have system with compact logix which is communicating with a PLC ie also a compact logix and 3 OPC test clients
from last few days i observe Alignment and FCS errors in port diagnostics can anybody tell me what is the effect of this errors on my system and how to avoid this errors?
 
Alignment and FCS errors are always the result of faulty Ethernet cabling or induced noise on the Ethernet network.

Inspect, repair, or replace your Ethernet cables, starting with the one connected to the CompactLogix controller.
 
I can't tell you how it's going to affect your system. FCS and Alignment errors indicate a noisy Ethernet link, and that's going to result in retries and timeouts at the TCP level, and probably also at the CIP level.

At best it will just slow down and cause small random delays in your system. At worst it will cause your system to fail to communicate reliably.
 

Similar Topics

Hello, I have a requirement to manage the text alignment dynamically. So, for example: 1. English Texts should be displayed from Left in...
Replies
0
Views
108
Hi, I'm not looking for code but rather some suggestions on how to approach this problem. I can see myself writing messy code when surely there...
Replies
10
Views
2,649
Hello, all! This is a PLC indirect question. I have trailers with conveyors inside which connect to dock conveyors when parked. The conveyors...
Replies
7
Views
2,653
Hello everyone, PFA. I am not very used to of the Insight system. But this is a general question, Since the 0 line is offset from the right edge...
Replies
0
Views
1,028
Anyone else have the problem where certain things aligned in the development environment do not align properly when testing the display or at...
Replies
7
Views
2,503
Back
Top Bottom