DavidBartel said:
...I have spent hours on the phone with their tech support to the point where they say the problem must be in my computer...
David,
NB: Since these modules use
DHCP instead of BOOTP make sure that the module has no access to other
DHCP servers, routers, etc. via your network, or a possible wireless gateway through your PC. Something on your laptop may be acting as a
DHCP server, and interfering with the BOOTP/
DHCP server.
Do you have more than one NIC (Network Interface Card)? Even a virtual one? If so, it's possible that the DHCP requests from the module are coming in on the NIC it's connected to, but BOOTP/DHCP is sending the replies to the wrong NIC. Unless you have more than one, I won't explain how to get around that.
Other possibilities beyond that are...
Windows Firewall - Allow BootP.exe through Windows Firewall
Antivirus software - Turn off all Antivirus software
VPN software - Disable VPN
Incorrectly set Subnet and/or Gateway address - See below
If all is ok, this is the method for setting the modules IP address.
- Register the 1799ER-1Q10X0Q10's EDS file using the EDS Hardware Installation Tool.
- Launch the BOOTP/DHCP Server.
- Click Tools then Network Settings then change the subnet mask and Gateway to their desired values. These will be assigned to the 1799ER module along with the IP address.
- When you see the 1799ER module's MAC address appear in the Request History list, right-click on the request and select Add to Relation List. The 1799ER's MAC address is listed on it's label.
- In the New Entry window enter the desired IP Address and click OK.
- The module should appear in the Relation List. Select it and click Disable BOOTP/DHCP to apply the IP address to the module's non-volatile memory.
PLC GURU said:
I could not get the bootp ->static to stick, power cycle would revert it. ended up using RSLinx and ethernet/ip driver to browse for the 1799er with its default ip address and switching(right click, config) it that way. I had another issue with a 1734 module and found that i had to set my computer to DHCP (instead of static with a similar IP address)...then my win7 computer had no issue using all of the bootp software functions.
PLC GURU,
I think you might be mixing up which method you ended up using for these two modules?
The IP address of the 1799ER-1Q10X0Q10 module cannot be configured using RSLinx. It can only be configured using DHCP through the BOOTP/DHCP Server.
The IP address of 1734-AENT(R) module cannot be configured using the BOOTP/DHCP Server. It can be set either by using the thumb wheel to set the 4th octet to 001 - 254, limiting the address to the 192.168.1.XXX class, or by initially setting a valid thumb wheel address and then browsing to it in a webpage and logging in to configure it a different class address. Alternatively you can right-click it in RSLinx and choose
Module Configuration. That goes for the 1794-AENTR as well.
George