Allen Bradley SLC5/03 Communication
Surrey Scada
May 2013
Surrey
I have a Allen Bradley SLC5/03 processor. I have a RTU connected to port 0. The RTU is configured as DF1 half duplex master, 9600 baud (these settings cannot be changed). I need to connect a second RTU to the PLC. This can be done with a port splitter on port 0 to share the port with the first RTU or a port splitter on port 1 to share port 1 with the second RTU and a programming port. I've tried the 1747 DPS1 and DPS2 port splitters but they don't support 9600 baud. Any ideas?
Richard
Is it a very old Allen Bradley Remote Terminal Unit? The comm settings in the newer AB DataSite Remote Terminal Unit Controllers can be changed.
This sounds like an unusual system; usually RTUs are the slave devices, not the masters. But it is what it is.
I don't think the port splitter will do what you want. As you have pointed out, the incompatible port speeds are a problem that might not be solvable.
My instinct would be to add a 1747-KE module or a Prosoft MVI46-DFNT module to the chassis and let that communicate with the new RTU.
If you want to pursue matching the port speeds and using the DPS2, you could try a baud rate converter like the B&B Electric 232BRC.
It is an old Micra Systems RTU that we are phasing out. The driver and protocol settings are not configurable. We are replacacing them with a Motorola Ace RTU, but need to run both systems side by side until all sites are upgraded.
Thanks Ken, looks like the 1747-KE will be the quickest and cheapest way to get another port. I'll give it a go.
Hey Everyone, I need to Interface Ignition SCADA ethernet network to an Allen Bradley SLC5/04 Serial RS232 DF1. Has anyone out there found a low...
993
Hi Guys, I've not used one of these PLCs for a while so am a little rusty, but a customer has one on an old machine that he needs help with. I...
1,901
Hi. We have mashine with AB SLC5/04CPU PLC and Proface AGP3500. I need transfer data AB SLC5/04CPU PLC to TSX momentum PLC using ethernet...
6,350
Hello chaps i wonder if someone could have a look at the attached file and try to guide me in the right direction as to a problem I have with the...
18
4,639
Iam having a problem with a program Iam trying to download to a new processor.I can connect with df1 download the program but then the comm port...
3,184