Good day everyone. I am installing a used machine with an Automax control and drive interface system. This rack has 2 processors a 57C435 and a 57C431 with a common memory module 57C413B. This machine was running 9 months ago when our guys unwired it. now on install and first application of power
the left processor the 435 displays dd which is done booting waiting on other module. 2nd processor is displaying 05 which is parity test failure. Any clue as what to do next?
 
I don't have anything to add other than to ask if you pulled and reinserted the cards? We had several of those systems and more than once a power up problem would go away by re-inserting the cards a few times.
 
OK looks like I need to reinstall the program. Next hurdle is, this is old stuff, the newest OS it can run on is Win98. I have a VM image of Win98. But I can't load in the Automax V3 software. It wont work with USB memory devices. Help, suggestions please!!!
 
I have it on an XP image but cant seem to connect to it.
What cable are you using to connect to the processor, A
USB to rs232 or a standard comm port?
 

Similar Topics

Good Morning All! I have a machine we recently install with an Automax control and Drive system. I need to maintain this and make improvements...
Replies
0
Views
613
We just got a new to us, used machine. It has 2 Automax racks with 3 Drives and associated I/O. How does a person print out the blk files to look...
Replies
17
Views
3,878
Hi all, i have system running reliance automax plc system and drive system. The scada systems are wonderware intouch ver 5.0b. the automax plc...
Replies
0
Views
1,453
Anyone seen remote I/O adapter with fault flashing and says "ESO LOS"
Replies
1
Views
1,449
Hi all, I have a very old reliance automax PLC system in a packaging machine, which we cannot upgrade now at this stage, the communications go...
Replies
3
Views
1,762
Back
Top Bottom