Hey guys,

A couple of quick questions but first a layout of what I'm working with.

Compactlogix 1769-L37erm controller. The current system we have is a micrologix 1400 that im trying to retrofit. that uses a integer register to hold a sequence number and gets incremented when a step in the sequence is complete. This also has bits to flag the start and end of a batch.

The HMI for the new unit will be Wonderware(Aveva) intouch 2020

1. Is there a better way to do sequences(about 100 sequence shifts max) in studio 5000? (I plan on running V30.11)

2. Should i make the batch portion part of an "Event" routine or just keep everything under a continuous routine like i usually do?

3. Also, I am having a hard time with the prosoft mvi69E-mbs availability. Is there a strong solution for compactlogix-modbus RTU comms out there? Imk aware of the data station, Moxa Gateway, and 1769-sm2(Not sure if this will work)
Here are the requirements
* 100 Commands (About)
* RTU only
* 38400 Baud
* 24 or 12V
*cabinet is small, so size may be an issue



Thank you everyone!
 
Personally, I would stick with the integer numbers, this is a great way of controlling sequences for many reasons, using bits (SET/RESET) can get messy, also it makes sense to make the steps in multiples of 10, that way if you need to add a step it becomes simple to slot one in.
Another good reason is on most Scada systems you can use a lookup (preferably an SQL table) where the step numbers equate to messages so to display what is currently happening the Scada does a query based on the integer for example 0 = IDLE, 10 = Start up, 20 is Adding xxx & so on, simple to add other messages so it displays what is happening on the screen.
 
the Spectrum Controls Gateway does a good job in modbus RTU to Compactlogix.
The GUI is a little wonky, but you can import a tag and device list to get around that.
 

Similar Topics

Hi Everyone, Thought I had it figured out but I came to the conclusion it would not work. Here is what I'm working with... 1769-L30ER Flow Meter...
Replies
24
Views
710
Does anyone have expereince creating a custom API to build a campaign management system for FactoryTalk Batch? Stuck between using a REST API or...
Replies
0
Views
472
https://literature.rockwellautomation.com/idc/groups/literature/documents/qs/iasimp-qs042_-en-p.pdf The video links in this pdf are not working...
Replies
1
Views
1,131
Can someone shed some light on what the connector is that allows Batch to connect to Historian and create historical trends based on batch...
Replies
0
Views
697
Complete novice trying to integrate an industrial fluid filling process into MES using an anybus communicator Hardware: Anybus Communicator...
Replies
3
Views
1,594
Back
Top Bottom