Confirming Siemens PC/PPI cable

whtrader

Member
Join Date
Aug 2006
Location
KL
Posts
37
Does anyone know how to test Siemens PC/PPI cable(6ES7 901-3BF00-0XA0) to make sure it is working? Also can we connect to a Siemens PLC S7-200 CPU 224 when it is run mode or should I stop it using the physical switch?
 
Does anyone know how to test Siemens PC/PPI cable(6ES7 901-3BF00-0XA0) to make sure it is working?
It should be easy. Select the wanted baudrate on the cable. Connect a 24Vdc power source to the PPI side of the cable, +24V at point 7, 0V at point 2. Connect the differential input of an oscilloscope to the points 8 and 3. Plug the PC side of the cable in a COM port of your PC. Start hyperterminal up and set the COM port to the same baudrate as the cable, 1 stopbit, even parity and no handshaking. Now if you type something on the PC, you should be able to see the bitpattern on the oscilloscope screen.
Also can we connect to a Siemens PLC S7-200 CPU 224 when it is run mode or should I stop it using the physical switch?
If it was necessary to place the PLC in stop mode to connect, it would be impossible to monitor the program. So the answer is yes, you can.

Regards,
 
jvdcande said:
If it was necessary to place the PLC in stop mode to connect, it would be impossible to monitor the program. So the answer is yes, you can.

by the way, if u r config the com port of S7-200 in "freeport" mode in program. u must place the PLC in stop mode, for S7 micro/win just support MPI/PPI/DP communication.
 
zeuszeus said:
by the way, if u r config the com port of S7-200 in "freeport" mode in program. u must place the PLC in stop mode, for S7 micro/win just support MPI/PPI/DP communication.
This is not completely correct. Regardless of what the programming port is used for in the program, if the PLC is in the STOP position then the port is always configured as PPI.
If you are using freeport mode on the PLC, then it is also possible to provide logic in your program to switch from freeport to PPI and back without putting the PLC in stop mode. You could make it so that the port is in freeport mode when the mode switch is in the RUN position and in the PPI mode if the switch is changed to REM, as can be seen in one of the examples provided by Siemens I think.

Kind regards,
 

Similar Topics

I have a machine that requires different sized change parts to run different products and having the wrong change part will cause a pretty serious...
Replies
13
Views
3,501
Hey me again. I have tried to make a simple analog program, where I make an input activate a "mov" function. I move...
Replies
1
Views
2,273
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
240
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
155
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
311
Back
Top Bottom