connecting several cpu's to a scada

Amr Hassan

Member
Join Date
May 2005
Posts
340
i have a project where i need to connect 6 s7 plc to scada on a profibus network , is it possible to use the port on the cpu to communicate if is already configured as a master for some slaves(i/o, drive,....) or i need to add a cp in this case
 
No. You need to have a seperate CP module (ProfiBus).
Connect all the S7 PLC through the DP port and use ethernet to connect to SCADA. or if you are looking out for only collecting the information from the PLC's and monitoring(no control) on a SCADA then connect all the S7 PLC and SCADA through ethernet.
 
Why can't what Amr suggests be done? Could he not connect the Profibus network to his SCADA PC using a CP5611 or similar card in the PC? I have done that with WinCC.
 
i know that i can use the profibus port to connect to a scada , the problem is the port in this case is slave , not a dp master
 
I don't understand. If you have a connection from a Profibus network to a SCADA computer, why can't you communicate? WinCC, for example, uses "S7 functions" on top of the Profibus comms.
 

Similar Topics

Imagine, if you will, a series of custom built modules (building size). Each module is setup with standardized control/automation equipment...
Replies
12
Views
5,640
I have 2 PLCs. One is networked to our plant, and the other is networked to the first PLC via a 1756-EN2T. I could easily get the second PLC...
Replies
3
Views
65
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
71
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
119
Hello, I was looking to store some values from our FactoryTalk Application using Datalog to a MariaDB. I see there is quite a bit of documentation...
Replies
1
Views
126
Back
Top Bottom