We have an Allen Bradley Powerflex 70 Device net drive connected to PLC5 1771-SDN module. The replacement drive is a much newer firmware so I need to connect to the 1771-SDN with my Laptop so I can use RSNetwork for device net. We do not have a 1203-GK5 module. Is there any other way to connect to it.

Thanks for your help
Bob
 
In general the way to connect to a 1771-SDN is to connect to the DeviceNet network.

The common methods, in historical order, are:

1770-KFD (DeviceNet/RS-232)
1784-PCD (DeviceNet/PCMCIA, obsolete and discontinued)
1756-DNB (ControlLogix backplane to DeviceNet. Get on backplane usually over Ethernet).
1769-SDN (CompactLogix 1769-L32/35 or later)
1784-U2DN (USB/DeviceNet)

The modern method that's best-supported is the USB/DeviceNet 1784-U2DN. They're pretty expensive if all you're trying to do is reconfigure one drive.

Another method that's very slow but may do what you want is to use the 1771-SDNPT Passthrough driver in RSLinx Classic. It will allow you to connect to the PLC-5 through one of its ports and then use a special feature of the 1771-SDN to access the network.

Why do you think you have to reconfigure the 1771-SDN in order to use a new-firmware drive? My guess is that it's because there's an electronic keying error (Error code 73).

If the problem is just an I/O size configuration error (Error code 77) then you should be able to resolve it through the PowerFlex drive's HIM module.
 

Similar Topics

I have 2 PLCs. One is networked to our plant, and the other is networked to the first PLC via a 1756-EN2T. I could easily get the second PLC...
Replies
3
Views
32
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
62
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
100
Hello, I was looking to store some values from our FactoryTalk Application using Datalog to a MariaDB. I see there is quite a bit of documentation...
Replies
1
Views
110
I haven't encountered problems connecting to a PLC through VM Ware but I am with this particular machine. I'm running Windows 7 on a Windows 10...
Replies
8
Views
250
Back
Top Bottom