Hello Guys,
I have a problem regarding with my PLC communication, I have a module card 1734-IB4, everytime I triggered the input ch 0, the light activated but I can't see the bit inside the rs 5000.
Thanks for the Help
Regards
Was is working before or is this a new addition?
What communications type are you using? (Ethernet, DeviceNet, etc.)
Is the POINT I/O adapter working OK? (Check its LEDs)
Is the POINT I/O adapter instance under the I/O Configuration in RSLogix 5000 showing OK? (No errors or faults)
If you have added an extra module(s) to the POINT I/O Chassis then you need to expand the Chassis Size for the POINT I/O adapter in the I/O Configuration.
This is done under Module Properties>General>Change
Regards,
George
Yes, IO are good, it was working before, eventually the signal from input card to plc is lost and i dnt knw why, in the card the leds are showing good when it was trigerred. By the i am using controlnet. Thanks for the reply
have used Studio 5000 to program Logix 5571. Initially the PLC was working fine. I am in Remote Run mode. When I download the program and enable...
1,465
i am trying to make me a home practice setup and i need a input module with some kind of switch. I see in the older PLC5 therre is a simulator...
2,060
Dear all, I a have issue with 1756-IF8 Module , I reading some Air pressure and temperature analog values from this card , I have total 4 Analog...
3,109
Is there a way to see what the actual field signal value is going into each channel of the Analog Input I/O card 1756-IF16? In other words, I...
3,694
I'm not a PLC programmer, so bear with me here ... I was making an AOI with a bunch of BOOL inputs and realized some of them were actually...
1,855