RoTaTech
Member
The logic seemed to convert nicely, and I had to make changes to the addresses for my AD and DA and 32-point input cards.
The current problem is the NT620 HMI shows the hex value of the timer and counter PV and SV, and DM registers.
Omron TS gave two suggestions:
There is a setting in CX-Pro for the CS1 PLC Properties: "Execute Timers/Counters as Binary. After I changed that I had to edit 57 timers and counters from TIM and CNT to TIMX and CNTX. Still no change to screen display.
I tried using NT-Link 1:n instead of Hostlink to the HMI; that gave Setting error HRxxx on many HMI pages, but still shows the hex values in the pages.
Can anyone here make any other suggestions?