Hello!
I'm working in upgrading an old c28k Omron to a cp1e.
My doubts are concerning the IO pins. I can see in syswin 3.4 the following inputs:
0.0 to 0.15 so I should convert it to 0.0 to 1.4. Correct?
Regarding the outputs, on the PLC they are marked 100, 101, 102 and so on, but on the program I can only see coils starting at 1.0, 1.1, 1.2. Should I assume that they are the outputs and convert them to 100.0, 100.1, and so on.
Bruno
Inputs for the CP1 go 0.00 - 0.11 then 1.00 - 1.11 etc.
Outputs go 100.00 - 100.07 then 101.00 - 100.07 etc.
http://accautomation.ca/omron-c20k-c28k-c40k-c60k-troubleshooting/
Addressing:
The K series PLCs used a fixed address system. A maximum of 10 16-bit registers could be used for each CPU unit for the expansion I/O units added.
Example:
C28K-CDR-A (CPU 16 DC inputs / 12 relay outputs) + C20P-EDR-A (Expansion 12 DC inputs / 8 relay outputs)
Channel 0 – Address 000.00 to 000.15 – 16 DC inputs CPU
Channel 1 – Address 001.00 to 001.11 – 12 Relay outputs CPU
Channel 2 – Address 002.00 to 002.11 – 12 DC inputs Expansion
Channel 3 – Address 003.00 to 003.07 – 8 Relay outputs Expansion
Note: You are correct. Outputs marked 100 on the C28K represent 1.00. They would convert to 100.00
http://accautomation.ca/omron-cp1h-numbering-systems-and-addressing/
The CP1 has the following I/O address locations.
Input Area - 0.00 to 16.15
Output Area - 100.00 to 116.15
The above links will also point to the manuals of each controller.
Regards,
CP1 has 12 inputs per channel only - 0 to 11 and 8 outputs per channel - to 7 only.
Addressing:
Example:
Regards,
Thanks for all the inputs, but this one was very good.
I have finished the upgrade and in fact is quite odd for me that in this old PLC the outputs are similar to the inputs! I had to use tags to avoid been confused with it.
Thanks again,
Bruno
I am sending Omron Text over devicenet to an AB GuardLogix Processor. I am having a difficult time converting the string to readable data. I am...
4,162
I am looking at a dead C20, and the owner wants to go AB, which is my preference too. I have not worked with Omron since trade school. I have...
2,932
guys, Please help. Ive been having a self study on PLC Programming , I use OMRON CPM2A. I want to program the high speed input from my...
5,408
Help! I'm not too familiar with Omron. I would like to know if there is an easy way to locate where the problem is in the program? I converted an...
7,991
Anyone have any ideas on converting the AB "sequencer output" command to Omron PLC? I've been working on this for a while and my brain hurts...
6,743
jerrydesaulniers
J