I am trying to put some delay timers for fault messages in some of our programs but some of the faults are in FB so they are written STL already. here is wat i wrote in ladder converted to STl and want to do the Same in the blocks but do i pick the in/out for my timer and do i select 5S timer or just timer

A bit 0
A bit 1
A T20
= coil1
L S5t#5s
Sd T20

I have tried this but it will not take the contact for the timer.


A #BIT0
A #BIT1
A #TMR1
= #COIL1
L S5T#3S
L #TMR1

If I change the A tmr1 to L tmr1 it will take it but cant afford for it to be wrong when i download it in so how do i do this?
 
Try this:
Switch to FBD/LAD.
Create a timer, add enable bit1,bit0.
Switch to STL.

You should have something like:

Code:
A Bit0
A Bit1
L S5t#2s
SD T10

A T10
= coil

Step.png
 
Last edited:
If you feel more comfortable in ladder, change the view to ladder, insert a new segment, this will appear in ladder and program in ladder.
 
I think ADFOX is right first you have to call the timer and then you can use the timers contact.

That's incorrect, you can look at the state of the timer anywhere.

The problem with the original code was he did not have a condition to run the timer.

A bit 0
A bit 1
A T20
= coil1
L S5t#5s
Sd T20

In this code, A T 20 is in the code to set coil1, the RLO could be used to run the timer would always be off, so in effect the timer is relying in itself to have timed out to start timing.

A bit 0
A bit 1
L S5t#5s
Sd T20

A T20
= coil1

would be the correct answer
 

Similar Topics

What are the pro's and con's of wiring a euro motor for wye or delta when you have both options? Do you gain any more or less torque with either...
Replies
15
Views
4,372
Hello, I still do not have equipment in to test. But the RTAC ladder does not have a timer reset coil. I wonder if a reset coil on Timer.IN is...
Replies
1
Views
101
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
107
Hi all, I have a simple question that I have overcomplicated and gotten stuck on. I have a variable, we can call it "light" that I need to stay...
Replies
4
Views
351
Question to anyone with ideas about my thoughts on upgrading a very vintage timer, which is being used to switch between 2 5hp domestic water...
Replies
14
Views
456
Back
Top Bottom