Need some clarification regarding the devicenet set up
PLC is CLX with 1756-DNB scanner, trunkline using kwiklink flat cable with the micro connector for the nodes (direct connection to the trunk).
25 nodes consisting E3, DSA and VFD.
Total trunk line is approx 25 meters only inside the MCC panel
Baud rate setting for DSA is (auto) cannot be set to fix
E3 plus is also same but got some confusion regarding the next parameter which is (nonVol Baud rate)
Drives are manually set -- @ 500Kbps
I use IAB for simulation, I had 55m of cumulative drop length and when I run the cable wizard and set to 500kbps got error.
But powering up the system there was no error and the scanner is healthy condition, however, there is no particular time and got E78 from 1 drive and next day or week another drive in fault. intermittent E78 on 5 drives.
Need some advise please
Thank you