dvc 6010 positioner

shkoko2000

Member
Join Date
May 2011
Location
cairo
Posts
296
I measure the voltage on dvc 6010 and found it 10 V but input supply voltage is 24V why did it happen? How the voltage drop from 24 to 10?
 
Remember this is a current loop. Your output device to the positioner (PLC / DCS) adjusts itself to the required value of current between 4-20mA and also supplies the required voltage to the positioner which in your case should be a minimum of 10.5 volts. The balance of available voltage (13.5 volts) is being dropped across the source (PLC / DCS output card) internal resistance and any other item in the loop (example zener barrier if any).
 
The positioner is a load. It does work which requires energy. It uses the energy supplied by the analog output current loop.

The current in a current loop is driven by a power supply capable of some level of voltage output. A load in an electrical circuit is a resistance. Some of the power supply's voltage is dropped across the positioner, because the position is a load.
 
The transmitter is a load but the current through it is set by your process measurement via the transmitter electronics . The voltage at the transmitter will also depend upon what else is in series with it in the loop such as zener barrier (has resistance) and PLC / DCS input card (has resistance). If all three of these items are in the loop then each will have a voltage drop. The total voltage in the loop would then be 24Volts = input card volt drop + zener barrier volt drop + volt drop in signal wires + (remaining voltage = transmitter voltage).
I think that you need to provide details of exactly what items are in each loop to proceed further if the above does not help you.
 
What point 3 is saying is that you need a minimum open circuit voltage from the current source (output card) of 10.5 to 11 volts (according to the positioner specifications) before you connect the positioner. Once you connect the positioner this voltage will fall to some value between 9 and 10.5 volts. The voltage difference after connecting the positioner will be dropped across the current source and any other items which are in the loop. If this 10.5 / 11 volts is not available to the positioner then you will not be able to drive 20mA through the positioner.
 
Do not put 24Vdc from a power supply directly into the (+) and (-) terminals on a positioner because it will damage a positioner.

A positioner is a load driven by a 4-20mA signal; it is not the loop's current regulator like a 2 wire transmitter, the analog output is the loop's current regulator.
 

Similar Topics

WE have several fisher DVC 6200 that will not allow us to force a signal to the I to P, such as we cannot send 4 milliamps to the it, we get a...
Replies
4
Views
1,692
I'm doing some work on a HTST in a dairy plant. I uploaded the PLC program in the once-sealed FDVC (Flow Divert Valve Controller). This...
Replies
3
Views
3,276
Hello! I have an Emerson DVC6010 positioner on the Fisher 667 valve. This positioner has an analog input 4-20 mA with HART protocol. I want to...
Replies
0
Views
2,341
I have a PLC chneider 171CCC76010 with pump 2 control program in attach file. can you please explain program?. i can't understand program under...
Replies
0
Views
1,512
Hi, I am using momentum plc (171CCC76010 PROCESSOR) and having one Modbus Port1 connector to communicate with my HMI or to download program from...
Replies
1
Views
2,068
Back
Top Bottom