Thank you so much for your effort in helping me address this strange issue.
I sent you the version with the bit set to 0, because that is the same state that I'm trying to upload.
I have a PIC here also, and via the PIC I am able to connect normally (with limited access of course), but assume that my connection is solid because I can change the run mode of the PLC. Both the PIC and UIC act exactly the same no matter what I try to do. I even have two notebooks and both are doing the same thing.
I have the CPU empty (EEPROM removed, jumped 14 and 28 together, and CPU listed as default in RSLinx) but I'm now fighting with one single problem.
Whenever I try to download my program, I get the same error over and over again, no matter whether I use PIC or UIC, it's always the same:
Download Failed!
Could not set max station address.
I no longer care about getting access to the program in the CPU. I have the replacement program nearly complete anyways. I just need this CPU to start acting like a new out-of-the-box CPU, and it's not.
I am currently onsite in Algeria trying to get this equipment online, so unfortunately I cannot accept your kind offer for sending me a replacement PIC. I very much appreciate your offer, it does mean a great deal to the reputation of a helpful public community such as this one. Thank you.
I have 4 - 5/01 CPU's here. 3 blocked (all with the exact same program - S:1/14 bit to 1) and one with different software unlocked (S:1/14 bit to 0). I can connect and exchange software with the unlocked module without a hitch. All three locked modules, whether reset/cleared or not are acting the same way. It leads me to believe that the S:1/14 bit is still affecting my access somehow. The original programs in all three locked PLC's function seem to be functioning correctly, but I expect some minor changes will need to be made prior to finishing the project and want to be prepared for it. I/O's are functioning properly as based on t so I really doubt I am dealing with a faulty PLC issue.
Tried Allen-Bradley's tech support email page last night, but there website doesn't seem to be working properly, so I cannot ask them what the error message means, and more importantly how to get rid of it.
I have been practically sleeping with this PLC (yes I take it with me to the hotel room in the evening) and think I have tried everything, but I have bluntly accomplished nothing. This error has been here from the very beginning on all three PLC's that have protection enabled.
Regarding the email, my apologies. I called our company ISP this morning to ask what was going on, and they delightedly informed me that last night they decided to move our mail server without informing us, so that will explain the delay in you receiving yesterdays emails.
I'm closer to accepting the fact that the most painless way out of this one (based on your successful test results) may be for the company to send me 3 new SLC's. I could have brought them with me, but I didn't imagine that I would be completely blocked from erasing and writing to an older unit. It will still bother me for a long time if I don't figure out what is going on here.
cheers,
erik
Thank you so much for your effort in helping me address this strange issue.
I sent you the version with the bit set to 0, because that is the same state that I'm trying to upload.
I have a PIC here also, and via the PIC I am able to connect normally (with limited access of course), but assume that my connection is solid because I can change the run mode of the PLC. Both the PIC and UIC act exactly the same no matter what I try to do. I even have two notebooks and both are doing the same thing.
I have the CPU empty (EEPROM removed, jumped 14 and 28 together, and CPU listed as default in RSLinx) but I'm now fighting with one single problem.
Whenever I try to download my program, I get the same error over and over again, no matter whether I use PIC or UIC, it's always the same:
Download Failed!
Could not set max station address.
I no longer care about getting access to the program in the CPU. I have the replacement program nearly complete anyways. I just need this CPU to start acting like a new out-of-the-box CPU, and it's not.
I am currently onsite in Algeria trying to get this equipment online, so unfortunately I cannot accept your kind offer for sending me a replacement PIC. I very much appreciate your offer, it does mean a great deal to the reputation of a helpful public community such as this one. Thank you.
I have 4 - 5/01 CPU's here. 3 blocked (all with the exact same program - S:1/14 bit to 1) and one with different software unlocked (S:1/14 bit to 0). I can connect and exchange software with the unlocked module without a hitch. All three locked modules, whether reset/cleared or not are acting the same way. It leads me to believe that the S:1/14 bit is still affecting my access somehow. The original programs in all three locked PLC's function seem to be functioning correctly, but I expect some minor changes will need to be made prior to finishing the project and want to be prepared for it. I/O's are functioning properly as based on t so I really doubt I am dealing with a faulty PLC issue.
Tried Allen-Bradley's tech support email page last night, but there website doesn't seem to be working properly, so I cannot ask them what the error message means, and more importantly how to get rid of it.
I have been practically sleeping with this PLC (yes I take it with me to the hotel room in the evening) and think I have tried everything, but I have bluntly accomplished nothing. This error has been here from the very beginning on all three PLC's that have protection enabled.
Regarding the email, my apologies. I called our company ISP this morning to ask what was going on, and they delightedly informed me that last night they decided to move our mail server without informing us, so that will explain the delay in you receiving yesterdays emails.
I'm closer to accepting the fact that the most painless way out of this one (based on your successful test results) may be for the company to send me 3 new SLC's. I could have brought them with me, but I didn't imagine that I would be completely blocked from erasing and writing to an older unit. It will still bother me for a long time if I don't figure out what is going on here.
cheers,
erik
geniusintraining said:Good morning everyone....
Erik emailed me the file.
OK, I sold my last 5/01 so I had to change and download the processor type to a 5/02, I also had to go from a 7slot to a 13 slot rack, I had all the cards but the last one and changed it from an OW16 to an OV16....
I don't think any of the changes should of made a difference as the program was not changed.
S:1/14 bit is low (0)
After the download went on line and to run with no issues....
So I have no idea on what the issue may be, other then something to do with the UIC, as I know nothing about them.
Erik, Do you have an real serial port on the PC? if so.... you pay for shipping and I will send you a PIC, if it works for you and you want to keep it then just pay me, if not send it back, but using a PIC you need a real serial port, not a USB
If anyone has any ideas or want me to try a few things let me know... I will be back later this afternoon.
Hope this helps.
Mark
PS, Erik the email said you sent it 12 hrs ago but I just got it this morning??? slow email