We have a S5 928B Processor, with an IM308B ET200 card. The profibus network has a 16I/16O ET200B IO module, an OP15, and a profibus Festo valve island.

The problem that we are seeing is that the inputs on the ET200B module - despite showing as constantly ON on the module LEDs - appear on a PG as zeros for most of the time, with an occasional flash of their actual values.

We have replaced the ET200B module, and its base. We have also removed the existing profibus cable from the ET200B module and IM308B. We put a test profibus cable between the IM308B and a replacement ET200B module with the same profibus address. A signal was put into one of the inputs of the replacement module, and when observed through the PG, that input displayed the same behaviour as previously seen. The input showed as a 0 with an occasional flash of its true value, a 1.

None of the other inputs on this profibus network (specifically from the Festo module) show this behaviour.

Rewiring the problem inputs into unused input cards on the main rack resolved the issue, insofar as we were able to get the machine running again, but the problem remains unresolved.

Any ideas what might be causing this please?

thanks,

Martin
 
Here, check the troubleshooting chapter thoroughly:
http://www.pacontrol.com/download/PROFIBUS_Guideline_Commissioning.pdf

And Profitrace is a super helper:
http://www.procentec.com/profitrace2/index.php

Kalle

Hi Kalle,

Thanks for the information. I'm making enquiries regarding the Profibus analysis tool.

Siemens said to me that because this was "old" Profibus L2 (via IM308B card) that there was no diagnostic information that could be got from the bus. Is this not correct?

thanks

Martin
 
Sorry, but I haven't worked with L2 the last 15 years so I have no fresh experiences to share. I can remember there was an FB that could read out status from the 308; if nodes were defined and if they were accessible on the bus. It wouldn't help you much with this mysterium.

Sinec L2 is the mother of Profibus DP, also running RS485, so the Profibus troubleshooting guidelines should be relevant here also. The issues with reflections, retransmissions, common offset error, grounding, signal voltage levels, line lengths, screening, EMC, and... are also close related, so the Profitrace should be suited. But better check with the dealer.

Kalle
 

Similar Topics

Processor: 1517F3; Software: TIAPV13. Application scan time: 1mS. I have several FCs which are unconditionally called in OB1. In one of them...
Replies
3
Views
2,398
Has anyone experienced a CV spike when the PV is already above the SP using a PIDE in a CompactLogix? Attached picture shows a trend recording...
Replies
9
Views
2,765
Guys, Does anyone has an idea why a group of conveyors running on Powerflex 40 controlled by analog signals could be going into erratic...
Replies
11
Views
3,833
On older Panelviews and on TCP QuickPanels when using a SLC5/XX, a message box or indicator that is controlled by an integer is updated at the end...
Replies
2
Views
6,360
the plc and the automation system consisting of motors and cylinders work fine most of the time. however, there's still erratic behaviour by the...
Replies
6
Views
2,363
Back
Top Bottom