Ethernet/IP MCC capacity per 1756-ENBT

curlyandshemp

Lifetime Supporting Member
Join Date
Jul 2005
Location
Toronto
Posts
1,903
We are bidding on an application where the customer has been convinced a Schneider Ethernet/IP based MCC is the best solution. There may be up to 200 drives and smart O/Ls in this MCC.

Is there a general rule of thumb on many Ethernet/IP devices should be connected to one 1756-ENBT? I can't find any documentaion in Rockwell's knowledge database.

For DNET Mcc's , I typically limit 32 drives &| E3 Overloads to one 1756-DNB.

In order to come up with a configuration, i need to know how many 1756-ENBT cards to add.
 
The answer varies depending where you look. According to Appendix C of this Manual.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/enet-um001_-en-p.pdf

The 1756-ENBT supports 64 TCP Connections. I believe newer versions may have added more connections.

Search for RA KB Article 40784 and 38352. There are also others, the search term I used was "1456-ENBT TCP connections". An 1756-EN2T may serve you better in this application.

No matter what the number of connections allowed, I would think you wouldn't want to load it fully. Hopefully, Ken Roach will Chime in here later today.

Stu....
 
The answer varies depending where you look. According to Appendix C of this Manual.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/enet-um001_-en-p.pdf

The 1756-ENBT supports 64 TCP Connections. I believe newer versions may have added more connections.

Search for RA KB Article 40784 and 38352. There are also others, the search term I used was "1456-ENBT TCP connections". An 1756-EN2T may serve you better in this application.

No matter what the number of connections allowed, I would think you wouldn't want to load it fully. Hopefully, Ken Roach will Chime in here later today.

Stu....

Yes, I am aware of the max # of I/O connections, just looking for a "rule of thumb" limit.

I know already to split out any HMI/SCADA/Programming /Remote support on one 1756-ENBT and put Ethernet/IP on its own 1756-ENBT.
 
It depends on how many connections the devices use. Drives mostly use 1 or 2 connections depending but this is based on AB you will have to refer to the Schneider literature to be sure.

No you don't want to tap out the connection because a connetion does not always release when it should and you consume connetions for produce and consume tags also plus software like rs logix will consume 1 or more connections depending.

Keep in mind also that all logix processors up to the L7x series could only handle 250 connections for the entire system so large systems need 2 0r 3 processors. I have 2 lines that have 4 L6x processors because of this limitation.

The new L7x series handles 500 connections EN2T would be better as they handle 128 connections.
 
Yes, I am aware of the max # of I/O connections, just looking for a "rule of thumb" limit.

I know already to split out any HMI/SCADA/Programming /Remote support on one 1756-ENBT and put Ethernet/IP on its own 1756-ENBT.

Sorry if I misunderstood your question, just trying to help.


Stu....
 

Similar Topics

Hi Guys, I am working on a project where we will have a Smart MCC from Rockwell. We have over 50 motors, anyway we have ethernet capable motor...
Replies
10
Views
4,643
Hello guys i'm working with an s7 1200 plc with an ET 200S expansion module. The problem is that i can't find the plc when searching in the...
Replies
1
Views
101
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
8
Views
285
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
108
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
325
Back
Top Bottom