A FlexLogix cpu 1794-L/34A is using a Ethernet module 1788-ENBT/A to communicate with several Flex-I/O racks and one Pro-Face GP2500S HMI.
When the HMI is connected the HMI returns the fault code 01:0204 from the PLC. This is and extended error code from the MSG instruction set, saying "Unconnected Message". This message appears after several (5+) hours and has been delayed from 2+ hours after changing the "Send Wait Time" in the comms setup for the HMI.
According to Pro-Face the HMI will communicate as fast as possible (for the HMI) with the cpu in order to update for alarms etc.
As I see it, the maximum of 16 messsage connections that the FlexLogix can handle at a time has been exceeded. Normally I would detect the problem in the cpu and pause the communication, but as the HMI is the one initiating the communication, I do not have that option - or what?
Any ideas to how to handle this situation?
When the HMI is connected the HMI returns the fault code 01:0204 from the PLC. This is and extended error code from the MSG instruction set, saying "Unconnected Message". This message appears after several (5+) hours and has been delayed from 2+ hours after changing the "Send Wait Time" in the comms setup for the HMI.