on your IFE setup screen you have the Data Format set for BCD - that needs to be Two's Complement Binary for a PLC-5 system ... I haven't had time to check the rest of your system - and I won't have any spare time until MAYBE tomorrow evening ...
also - you should be aware that this type of module has jumpers inside it that must be properly set to configure the individual channels for "current" or for "voltage" - and for "single-ended" or "differential" wiring ... have you checked those jumpers? ...
in the meantime, change the Data Format and see if things start to fall into place ... there's a good chance that this is the biggest part of your problem ...
PS Edit ... I just noticed that you have some of the "Range" settings entered for 0 to 20 mA (etc.) - instead of for the 4 to 20 mA signals that you mentioned ... double-check those settings too ...
hope this helps ... signing off ...
.