Well, i checked lots of things and eventually got someone at Siemens Tech support to get back to me.

The motor was not going overspeed at all, it would just stop. We have an input transformer before the drive and the voltage is relatively noise free at this stage.

After checking many things suggested to me and finding nothing wrong, the Siemens tech guy told me to mask the fault in the drive so it would not trip...

I'm not happy with the solution but he seemed pretty confident that this thing happens resonably regularly with spurious faults of this type and masking it would not cause any problems for the drive, motor or machine.
 
A couple things can cause that fault, some of which have been mentioned here.

I would meg out the motor, and make sure it's not developing any paths to ground to start.

Aside from that,

1) You say it's in dancer control, that does NOT have to be in speed mode. It is very common on those drives to use pure torque control while in dancer mode. If that is the case, overspeed can easily be tripped if the dancer feedback device or cabeling is getting intermittant.

2) Intermittant field connections will cause that problem as well.

3) A bad power/interface board, or A/D converter on the micro-board can also cause random FO38's.

The more common fault on 6RA24's operating in speed mode is F031, which is a speed regulator ref/fbk mismatch.
 

Similar Topics

Hi, I'm trying to set up a Siemens Simoreg DC-Master on devicenet without using explicit messaging. I can't figure out exactly how the eds file...
Replies
0
Views
5,895
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
482
Hi all, i am the new controls guy at the plant and i have inherited a pc from the previous controls guy with Siemens tia portal version 16 and 17...
Replies
20
Views
970
Hi, I have a customer with a S7300 from around 2013 which they link to approx 25 inverters, 3 DP to DP converters and 5 IM153 remote I/O units...
Replies
8
Views
343
Hi all, First, thank you for reading the thread. So I had a task as the following: An up-counter must be programmed as part of a batch-counting...
Replies
7
Views
329
Back
Top Bottom