Honeywell Udc3300
bwiring
Nov 2005
mpls. mn.
66
Can Anyone Tell Me How To Set A Honeywell Udc3300 Temp. Controller To Continuly Tune It Self. I'm Using It To Ramp Down To -285f And It Seems To Over Shoot The Sp. On The Way Down. Once It Warms Back To The Sp. It Holds A Steady Temp. It Is Setup In Pid-a Mode. Thanks For Any Suggestions.
Try the dual PID option first. It's promoted as a feature so you can have one PID for heat, and the other for cool, but it doesn't matter. The controller will switch to a different PID based solely on a setpoint.
Tune the second PID at -285F. Switch to the second PID about 5-10% into your last rampdown. You don't want it to switch PID parameters at a setpoint, or it will 'hunt'.
Fuzzy Logic was the wonderful new thing that was going to save the world, but it didn't turn out that way. Some are better than others, but most will agree nothing can replace a well tuned PID.
Try it to see if it helps, but don't be surprised if it's not perfect.
You can't always trust Autotune. Use it to get numbers close, but don't be afraid to do a little manual adjustments to get it perfect.
You want to initiate autotune on an approach to the final setpoint, for your case, when ramping down. Is that how you've done it in the past?
Dan
Can anyone tell me if the ctrl 1 on a honeywell udc3300 can be used as a contact instead of a 4-20mA output on model number...
1,320
One of our customers has a Honeywell UDC3300 with 2 current outputs. It has worked well for years controlling 2 Fisher valves to maintain water...
3,863
Hi Anybody knows how to enter Honeywell HMI config menu. I need to change date and time of HMI. HMI series: Honeywell HCi series
121
Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
73
Hello, I am learning to create shapes and VB Scripts in HMIWeb Display Builder. I wanted to change color of my rounded rectangle by script. I...
124