How many Slave devices can I connect

daon

Member
Join Date
Jan 2012
Location
Sofia
Posts
1
Hi,
Do any of you know how many slave devices I can connect to AC500 or AC500 eco via modbus RTU.
Thanks in advance,
Nikola
 
In the 1990's and early 2000's, Modbus RTU (RS-485), generally used 15 or 16 devices as the limit. Some time after 2000, that number increased to 32 slave devices.

Modbus/TCP over ethernet uses IP addresses, so routing via gateways is more of an issue than the number of devices on a particular subnet.

An RTU master probably has a spec, but it's caveat emptor (buyer beware) as to a spec for ideal conditions vs reality.

The number of devices is empirically determined by the ability of the each slave device's electronic line driver to drive the line, the amount of noise for where the network runs, and biasing and line termination issues.

All of which combine to say that the manufacturer can claim a high number of slave devices that works on a bench top, but under operating field conditions, that number might drop dramatically.
 
In the 1990's and early 2000's, Modbus RTU (RS-485), generally used 15 or 16 devices as the limit. Some time after 2000, that number increased to 32 slave devices.

Modbus/TCP over ethernet uses IP addresses, so routing via gateways is more of an issue than the number of devices on a particular subnet.

An RTU master probably has a spec, but it's caveat emptor (buyer beware) as to a spec for ideal conditions vs reality.

The number of devices is empirically determined by the ability of the each slave device's electronic line driver to drive the line, the amount of noise for where the network runs, and biasing and line termination issues.

All of which combine to say that the manufacturer can claim a high number of slave devices that works on a bench top, but under operating field conditions, that number might drop dramatically.
Plus there is 1 byte allocated for the address which means a total of 256, 1 is needed for the Master and several are predetermined. IIRC there are 250 addresses available, but that does not mean that all master devices are programmed to use them all, that is another piece of information that reading the documentation should reveal.
 

Similar Topics

Good Evening , We have a number of Powerflex 525 Drives . I took notice for years elsewhere and our plant , that our Powerflex 525 drive...
Replies
0
Views
650
Good Afternoon, Just wondering , are many of you using SAP in your plants ? If so , is it difficult to learn ? Are there many training...
Replies
10
Views
1,435
It better to have too many instead of not enough right?
Replies
26
Views
2,913
Hi all- I have an application where: - I have a fixed system with a pre-determined, static, network (say, 192.168.2.0/24). - That system...
Replies
13
Views
4,248
I have an application that needs 20 inputs and 20 outputs with only 10 XNOR and 10 NAND blocks. I could do it with relays, but this could end up...
Replies
16
Views
5,182
Back
Top Bottom