Hello everybody

I have a problem with my comunication between FSGateway and OPC.
I have following the help document, and I have configured FSGateway, in diagnostics everything seems be fine.
But when I try runtime this appears "see screen shots"
any suggestion.
Thanks

FSGateway.jpg
 

Attachments

  • FSGateway 2.bmp
    275.4 KB · Views: 34
It looks like you need to "Activate" (start) the Archestra.FSGateway.1 I/O Server. Right click on it and click "Activate Server". In that same menu you can configure it as an automatic service, so it will start with every boot.
 
It looks like you need to "Activate" (start) the Archestra.FSGateway.1 I/O Server. Right click on it and click "Activate Server". In that same menu you can configure it as an automatic service, so it will start with every boot.

Thanks you for your answer, but not,the same warning.
any other suggestion
 

Similar Topics

Friends as the heading shows i want to integrate rslogix 500 with rsemulate 500 and rslinx opc server with fsgateway to see data in intouch...
Replies
1
Views
2,114
Hi There. I try one more time :) How do I send data using FS Gateway from Intouch to MS Excel on a secundary computer? Right now I use a script...
Replies
4
Views
4,109
I have S7-300 profibus,connected to a PC with Intouch and fsgateway, now I need to connect a CompactLogix L32E with Ethernet, as I can pass data...
Replies
0
Views
1,887
Hi All, While I appreciate the following problem has a lot variables, and as such, we are currently proposing alternative solutions to the end...
Replies
5
Views
6,070
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
136
Back
Top Bottom