Dear all,

I'm a using a flow meter for first time in my life, attached is the name plate details of krohne make flow meter.

In this 4-20mA is used for measuring current flow value and pulse output is used for accumulated flow volume.

I do not know how to use this pulse output. How do I make any sense out of it? It is written that pulse output is passive. Do i need to supply any power to it?

There is also a contact/ status output in this flow meter. what for this contact/status output is provided.

Thanks in advance,
Charz

IMG_0731.jpg
 
In general terms:

An active output gets it electrical power from whatever electrical power powers the instrument (flow meter). If you put a milliameter on an active 4-20mA output, it will show some current in the 4-20mA range.

A passive output uses a different dc power supply than the one that powers the instrument. This is done reduce the likelihood of common mode ground loops. If you put a milliameter on a passive 4-20mA output that does not have a DC power supply in its circuit, the meter will show 0mA, because the loop is not powered.

An output that uses 'kHz' is a frequency output. The output is generally used for flow rate, for example where a configured 0-5kHz flow rate for 0-100L/s would show 5kHz at maximum flow rate (100L/s), 2.5kHz at 50% of flow rate (50L/s) and 1250Hz (1.25kHz) at 25% of flow rate (25L/s).

Status shows events like alarms, batch total achieved, things like that.

A pulse for a given flow total, for example one pulse per 100L is done either on an electromechanical relay output or a solid state discrete output.

The outputs of flow meters of the grade can be configured (via a keypad or HART) for what their function can be, then determine how it needs to be configured for what this application needs to do.

You need to look at the wiring output diagrams and the function diagrams for each of the outputs.
 
Last edited:

Similar Topics

Hi folks, I am trying to fetch data from flowmeters of Krohne make using mlx1400 over RS485. The architecture as follows: Krohne device -----...
Replies
8
Views
1,387
Hi friends, I have a krohne flow meter optiflex5300. During liquid flow when it shows the actual flow value 2000 ml, physically its 2200 ml. I...
Replies
2
Views
1,866
Hi when i add the IFC 300 GSD File to Siemens CPU 300/ 400 Hardware Cataloug it appear in profibus PA Subgroup instead of Profibus DP.Is there...
Replies
0
Views
1,851
Hi, We have a krohne flow meter which controls the modulating control valve on our Blending machine which is electronically fault.We are in a...
Replies
2
Views
1,600
Hi! I has found two completely identical devices, one from VEGA, second from KROHNE. VEGASON 61...
Replies
0
Views
1,532
Back
Top Bottom