Laptop to Slc 5/03 via 1761-net-eni
Tom Hemeon
May 2007
Stratford, Ontario
18
Can you do online programming with a computer connected thru a 1761 NET-ENI to the serial port on a SLC 5/03. The current DH485 has become totally unreliable with a new DELL.
Having hooked this up I can see the ENI module on Linx but not the PLC. The serial light on the ENI module is flashing but the light on the PLC is not. If I remove the AP00 cable from the PLC and connect a serial cable to the PLC it hangs my Laptop and I have to reboot, after which I see the PLC again. The Laptop, ENI module and the PLC are set the same at 19200. Any ideas?
It's been my experience that you have to use the AB_ETH not AB_ETHIP driver in RSLinx. With ETHIP driver, I would see the ENI module only. With the ETH driver, I would see the PLC only, which is what you want. This was with Micrologix but SLC must be the same.
Please let me knwo how your are connected first of all
Your PC serial port is connect to the ENET module through _________
And ENET module is connected to SLC through ____________
Make sure the routing table on the ENET module config utility is properly configured. There should not eb any conflicts with node numbers.
As I said earlier I have tested the DF1 19200 serial communication between the PLC and the laptop and it is fine. I have no problem seeing the ENI module in LINX but I can't see the PLC 5/03. I even tried setting the baud rate in the ENI manually to 19200 as suggested by Allen-Bradley.
šŸ™ƒ
Problem solved. I switched the Control line in the PLC 5/03 Channel Configuration - Chan 0-System from Full Duplex Modem to No Handskaking.I have attached screen captures of all the settings of the PLC and ENI.CHANNEL CONFIG.jpg
Good Morning , I just purchased a Windows 10 Hp Laptop. Of course no serial ports , but 3 USB ports . Need a USB to Serial cable to go to...
20
6,339
Hey guys, I'm trying to connect my laptop to an old SLC500 PLC. It has a DH-485 port on it and I have to configure a driver for it on taking. I...
1,421
Hi guys. I'm working on building some screens for the pv500. The program is currently running in the SLC 5/01. I'd like to get my laptop online...
2,807
:) Hi everyone i am trying to get a laptop to communicate with AB slc 503, 504, 505, micro-logics 1100, and 1200 so far that I know of. Of course...
3,964
:hmmm:Its been a few years since I been involved with booting up a RSLoxic 500! I never had to use a laptop! now I do. I need step by step in...
2,225