Logix5550 Controller Clock status file

dpancipanci

Member
Join Date
Mar 2006
Location
San Pedro Laguna
Posts
18
Hi to Everyone,

Anybody knows where can i find the clock status file of Logix5550 controller (1756-l1/A)? These clock same as in SLC 5/04 s:24,25 & 26 if I'm not mistaken. Thanks.


Dante
 
You have to use a GSV (Get System Variable).

Set up a array tag (DINT 7 Words)like PLC_Time

PLC_Time[0] = Year
PLC_Time[4] = Minute

Do a search on the help files in RS 5000 for more help.
 
GSV Command
GSV.jpg


edit: Damn.... I really must get quicker on the keyboard!
 

Similar Topics

If we upgrade the firmware of logix5550 controller online from v5.16 to v13 what will happen?? I dont have the back up program im trying to...
Replies
4
Views
1,635
I am trying ti config and communicate with my 1756-L1/A. In my processor box on my software application, this processor is not listed. How do I...
Replies
3
Views
1,886
i am doing a student project at the moment and suddenely the PLC are not response to the Touchscreen.... and i check the program and find this...
Replies
1
Views
1,621
Hello! If someone can help me with the following problem. I can't change the phone number. Do I really need the interface (AL-232CAB - Programming...
Replies
0
Views
47
I have Woodward Controller EASYGEN-3500XT and Phoenixcontact make IO CAN-CUPLER part no: 2702230, Analog Input card: 2861412, Analog Output Card ...
Replies
0
Views
39
Back
Top Bottom