Can a low voltage electrical panel be designed to be opened without powering it off first without violating any electrical codes?


Panel will have 120VAC and a max current rating of 20AMPS. All AC terminals will have finger safe guards and or clear shields that will require them to be removed using a tool in order to gain access to AC components. 90% of the panel contents will be 24VDC controls & I/O wiring.



Thanks
 
It's supposed to have an interlock to prevent it from being opened while it's energized, except when defeated with a tool. Normally this is done via the disconnect whose handle is mounted through the door. Most disconnects are designed such that a screwdriver can defeat the interlock and allow the door to open without opening the disconnect itself.

But with only 120VAC, I'm not sure I'd even worry about it assuming it's in an industrial environment and the door has clamps that require a screwdriver to open.
 
I don’t think it’s too much of a code issue, it’s more of is the panel labeled with boundaries and appropriate PPE requirements.

I think it’s all listed in NFPA 70e.
 

Similar Topics

I have a 30 year old Symax PLC. Lately two of the outputs are putting out approx. 8vac continuously without the output being energized. All the...
Replies
4
Views
2,249
I have a analog card 1715-IF16 with six 4-20ma instruments on it. The card in a single-ended method. The instrument has been service for a while...
Replies
8
Views
2,491
Good afternoon, I have an Allen Bradley PLC 1768-L43 with one 1769-IQ32 input card and two 1769-OB16 cards (all three on the right side of the...
Replies
19
Views
7,866
Hi All, I have a project at the moment with a Festo PLC to be sent to the states. It must adhere to UL standards which I am not familiar with...
Replies
6
Views
2,373
Good Evening , I have a Guardmaster Safety Relay I have 14 vdc on S12 (Safety Input for IN1 Channel 1) and on S22 (Safety Input for IN1...
Replies
1
Views
3,559
Back
Top Bottom