We have several Siemens basic panels in use on a production line. The line was bought from over seas and so all the display screens are using metric where any units of measurement are displayed.
All the units of measurement are metric in the PLC program, but there is a conversion button on the HMI's to convert all the displays to show imperial measurements.
One of the contractors said he did the conversion in the HMI program, and I didn't really ask how.
It's been almost 2 years of running now, and I have the need to understand how this was done. I've made some minor changes on the HMI's, but nothing like this.
I am using TIA portal v14.
Can someone help me understand how to do this within the HMI program?
I hope this request is clear. (Ex. - PSI --- kPa)
Thank you very much.
If you can post a ZIP copy of the HMI program someone would be able to tell you exactly and where the conversions are done.
If it's a comfort panel, likely just using a scrip to scale or not scale the plc tag to an internal hmi tag for display based on a bit toggled by the metric/inch button.
you must have the source program.
Open the project in TIA
Select HMI / HMItags / Show all tags
Select the variable you want to convert
* In the "inspector window" select "Linear scaling"
you have a pair of values in the PLC and on the right the pair of values that you will see on HMI
This site has helped me many a time so I wanted to give back with something I worked on recently. I needed to set up a PV HMI in FTME that was...
1,415
Hi everyone. Here is the question! How a PID works on a Loss in Weight feeder? Gravimetric feed and Volumetric feed as well. What calculations...
2,273
Hello everyone, I am working on a new PLC project wherein the customer wants us to implement a face recognition biometric system that will...
2,656
Hi all, Does anyone have any suitable links to products which can be used with a Siemens 1200 PLC. I am struggling to find any suitable, in an...
2,852
I am using a GE quickpanel+ and connecting it to an Allen Bradley PLC. I have a lot of tags that I am reading from the PLC and displaying on the...
1,994