micrologix 1100 analog input
is the analog input on micrologix 1100 only for 0-10V ??
The embedded analog input is, with a 10bit resolution ( 0-1023 counts)
Just put a resistor across the input terminals 250 ohms gives you 1 to 5 volts, 500 ohms gives you 2 to 10 volts.
You can add an analog input module also. To accept the 4 to 20ma and give you better resolution.
I just have a quick question on this processor. I am making a project with 18 analog inputs so I bought 4 - 1762-IF4 expansion cards and the plc...