Hello all,
I have a micrologix 1400 with 3 expansion modules, an Analog Input (1762-IF4), a relay output (1762-OW8)and an Analog Output (1762-OF4).
I can only hook two modules at a time...whenever I hook up the third module, the PLC FAULT light and POWER light flash intermittently for about 1sec....the ethernet network lights also flash for about 1 second intermittently....the plc never boots up
I can mix and match the modules, but only two work..never three....so nothing seem to be wrong with the modules themselves...
Only other thing to note, is that I have these hooked up on a desk, for programming, not on a DIN rail...so maybe grounding is a problem?
any idea what is wrong?
thanks,
Ian
Ok, I just realized something..
The Analog Output Module works SOMETIMES....the other two modules work all of the time, so I guess the problem is with the Analog output module...
I checked on the bus terminator, but I don't see anything like that for the micrologix 1400..good suggestion though! thanks.
Sorry, I should have checked. I am used to the 1500. According to AB, the 1762 I/O doesn't require an End Cap with the 1100/1200/1400.
Stu....
What is a bus terminator?
I see references to a "bus terminator" for 1762 I/O modules for the Micrologix 1400.
I am doing a project using a ML 1400 and just added an -OW8: relay output module.
Do I need some other component called a "bus terminator" ? I know some systems needs end-of-line resistors for impedance terminations. Is this the case here?
No you don't need a bus terminator for the 1400.
81
122
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while...
236
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
338
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
702