Hi im new in that forum.I try programing mitsubishi fx3u and fx2n 8a/d.
When i set up a/d module to read volts is ok, but i can not read mamp.
My code to set module is TO k0 k0 h3333 k1 it is mean i set up ch1-4 to read mamp. Is it correct or im wrong?
Also i connect input V+ and I+ togheter.
Thank you for any help.
Hi artmierz,
You have made it right.
BFM # is for the first 4 input signals
H3333 = 4-20mA for CH1-CH4, so that is also ok.
Connecting V1+ and I1+ together is also ok.
Now how do you measure voltage?
Do you have an instrument/transmitter 4-20mA to test with?
Try read the BFM#29 = Error status.
What is the value/ what bits is on.
Can you upload your program or make screendump of the analuge program.
Best regards
Dariusch
Hi. I get sensor witch give me value from 4-20m apm.
To read volts i use second A/D module fx2n 8a/d.
And i write code:
TO k1 h1111 k1
i did not check buffer 29, but i will play today.
Also how i can check it?
I use gx works2.
exactly:
m8002------[to k0 ko h1111 k1] set up first module to volts ch1-4
m8002------[to k0 k1 h1111 k1] set up first module to volts ch5-8
m8002------[to k0 k2 k100 k8] average time 100times/sec.for 1-ad
m8002------[to k1 k0 h1133 k1] set up second module ch1&2 -mamp, ch3&4 volts
m8002------[to k1 k1 h1111 k1 set up second module ch5-8 volts
m8002------[to k1 k2 k100 k8] average time 100times/sec for 2-nd module
m8000-----[bmov u0\g10 d3 k7] read 7-data from first module and store in d3-d9
m8000-----[bmov u1\g10 d1 k2] read data from second module and store in d1-d2
Hi artmierz,
GX Works2
Go to "Online" -> "Monitor" -> "Device/Buffer Memory Batch"
Click "Buffer Memory" -> Type in adress for module and the BFM# = 29
And you are sure the sensor is working?
Have you measured mA on the wires to the module?
It should show min. 4mA.
/Dariusch
hi all, I'm wondering if anyone has ever converted an Allen Bradley AOI to a Mitsubishi Function block. I's hard to find libraries from...
18
Hello, I have a Mitsubishi FX3G 14M PLC and a E615 HMI from Mitsubishi/Beijer. I'm using GXWorks 2 to do the programming and I have no problem...
149
Hello! If someone can help me with the following problem. I can't change the phone number. Do I really need the interface (AL-232CAB - Programming...
69
how to communicate FactoryTalk Optix and Mitsubishi Q Series. I want to know the details of that
70
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
81