Modbus Plc (koyo)
h_wings
Sep 2002
Kuala Lumpur
I am try to use the KOYO PLC DL250 port 2 (MODBUS) communicate with a meter reading device. The device address is stsrt from 0000h. But when I want to communicate it with the PLC I can't see the value from PC. Any body have any idea?
Is the port on the D2-250 a master or a slave?
If it's a slave, the problem is most likely in the setup of the port parameters (baud rate, parity, etc), the RTU address, or the cable. If it's a master, you have the added possibility that there is something amiss in the ladder logic you've set up to manage the communications.
Are you getting any error codes at the master?
Two other things to check with AutomationDirect.com's tech support. First, the 205 supports more commands as a slave than it does as a master, so make sure the command you are using is available. Second, the very low addresses of some Modbus devices are not accessible to the Koyo because of the way they convert addresses. Make sure the address you are reading is available.
I assume you have verified the com link is working using a PC and a terminal program or such.
Hi all ! I can't figure out how to setup the modbus RTU comm. to connect a Koyo DL250-1 CPU with a Panelview Plus 600 from Allen-Bradley. I use...
3,984
Hey guys, I have one of the new CLICK plc from AD with an ethernet port on it. I made a subroutine for an IO Map of a modbus slave device I have...
4,709
I want to communicate my Q series PLC with Factory IO using GX works 2 software, I want to use modbus as server and the ips are as follows plc...
71
Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
114
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
32
958