Hello,
I'm in need of a solution to send data from RSLogix5000 PLC to a couple of heating controllers that have an RS232 Modbus interface.
Some point I/O is already on the machine and I came accross this Prosoft ILX34-MBS232 module.
http://www.prosoft-technology.com/P...tLogix-L1-and-Point-I-O-Adapters-ILX34-MBS232
Does anyone have usefull experience to share or a better alternative?
Thanks in advance,
Nick
Hi Nick,
I have used the RS485 version of this device with good results.
Fairly easy to set up if you are used to the Logix 5000 enviroment.
Prosoft technical support is also very good and free.
Hi Nick,
I have also used the Anybus communicator from HMS.
It sits on Ethernet IP (EDS files/AOP profile are supplied) and supports Modbus serial and RTU.
http://www.hms.se/products/abcrs.shtml
I found this more difficult to initially set up, but technical support was from Sweden and ok.
Once set up, it worked very well, even with large amounts of data.
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
53
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
236
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
273
Hi, I'm having an issue with a mircologix not transmitting out. The current setup is a mircologix 1400 connected to a Guardian 100 Radio...
119
If a device has Modbus RTU over serial and Modbus RTO over TCP and Modbus TCP then there is a difference between Modbus RTU over TCP vs Modbus TCP...
525