Motor winding identification
silva.foxx
Dec 2004
North Wales; always West to England!
519
Spurred on by this post ( http://www.plctalk.net/qanda/showthread.php?t=26742 )
Can anyone explain how you would go about identifying the windings of a three-phase single speed, 6 lead AC induction motor?
It can be worked out which pairs of leads are the windings with an ohmic check but how do you find the correct orientation of each winding?
I once heard it can be done with a battery and galvanometer... but how?
This is how you do it....
Step 1. Identify the 3 pairs of windings. This is easy, using a multimeter. Mark the ends A,A, for the first pair, then B,B, then C,C etc.
Step 2. Obtain a LOW voltage A.C supply. Around 10 volts will be sufficient. {Note that this will only work with an A.C. supply, not D.C.}. Connect this supply to the wire A,A. but do not turn on yet.
Step 3. Pick one end of the pair B,B, and connect it to one end of the pair C,C. With the remaining wires (one B and one C) connect to a multimeter set to volts AC.
Step 4. Turn on the supply. Check for a voltage reading on the multimeter. Now please note the following carefully...
The motor windings are referred to as "Starts" and "Finishes". If the connection between B and C is a "Start" joined to a "Finish", you will read a small voltage on the multimeter.
If no voltage is present, then the connection between B and C is a "Start" joined to a "Start".
If no voltage is detected, swap one of the wires at the connection between B and C.
Step 5. Lets say you have successfully produced a voltage..Should be around 4 volts..Where did this come from?? {I dont want to sound like a smart a$$, but this is important} If you get to the stage whereby a voltage is produced, then mark the B wire at the junction with C as B1. Mark the C wire at the multimeter as C1. This will give you the relationship between the B and C wires.
Step 6. The above procedure needs to be repeated for the A,A wires....
{Step 6a. Post back here if you are unsure of the steps outlined above}
Step 7. Join the wires A1, B1 and C1 to make a STAR (in Oz) or WYE (in USA) connection. Apply your 3 phase power to test your motor...Get ready to turn it off quick if something goes wrong!!
Good luck
Ian
Good to hear back from you.
This is something that I did not learn during my apprenticeship (training), but learnt many years later when I went back to college as a teacher...
It is something that every electrician should know how to do, but not many do.
Cheers
silva.foxx said:
IAN
That is perfect! It works... great. It's my new quiz for the workshop guys.
Many thanks.
Not a good quiz test, those that can do this are far beyond the average electrician.
The DC battery test may have pertained to something in your past for DC motors, there is a method for this.
This is something you know or learn in time, not something anyone would know...note: you did not, why put it on a test? If someone knows it they may take your job.
or there is the brave way.................assuming you have found the pairs
connect it in star, you have now either got it right or one winding wrong.
Try a quick power on - it buzzes, swap one pair - it still buzzes - put that pair back as it was and swap another pair - do this until bingo - or no motor lol.
It works because i remember doing once a long time ago
Whoa there horsey!
Chill Ron, don't read into this formally. Read "I'll put it on a test" as "Look at this, lads, a cool trick you may never need!" Also, who said my colleagues are only avarage electricians? Let it ride.
Now what if the motor has 9 or 12 leads and 6 windings instead of 3, and all of the wire markings are missing?
Does anyone else know the technique for identifying all 9 leads of a 3 phase 3-winding motor? (In a 9-lead motor, 3 leads are connected internally and are not normally accessible).
Hint: To do it by hand requires about 64,000 tests!
well,,hopefully it wouldnt take that many trys,,ill be willing to bet(unless you have murphy working against you) youll find it in many less tries
Fred Raud
Good Evening , Looking to upgrade and automate our motor rewind shop . I was on YouTube looking at some automated coil winders .Who are the...
1,195
Hello guys, I am facing the ground fault problem often. We have a liquid mixer machine and the motor is installed under the mixer tank.so...
26
5,774
I have a customer with an old pump panel which uses autotransformer style reduced voltage starter. I have worked with wye/delta starters, but...
1,708
We installed 4 new conveyors. All 4 have new 1.5 Hp motors and all 4 have new Powerflex 40 VFD's (22B E3PON104). After 24 hours running one of the...
24
10,371
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
290