Panel View Communications Module Replacement

KEE-ITT

Member
Join Date
Feb 2008
Location
Virginia
Posts
2
I would like to change a Panel view (2711-T10C1) configured to communicate RIO to a different format. The communications module appears to removable. Does anyone know where I can purchase a replacement and procedure that will allow the Panel View to talk DH+ serial to an Allen Bradley 504 CPU or ethernet to an Allen Bradley 505 CPU?

Thanks,

Kevin
 
Hi Kevin,

Not sure it is possible to swap communication modules on the PanelViews, seem to remember trying to do this a few years back and finding out it was not possible. The newer PanelView Plus allow you to add/change communication modules I believe. Maybe some of our more enlightened contributors on this site may be able to shed more light on this for you.
As a matter of interest why do you want to change from RIO between the PV1000 and the SLC?
 
KEE-ITT said:
The CPU505 that I have does not connect to the RIO port on the PV1000.

If you have a spare slot in the SLC chassis have you considered a 1747-SN RIO Scanner module?
 

Similar Topics

I would like to upload a copy of the Pb32 program on one of our legacy panel views(2711-T14C3) 1400. We currently have it connected to a SLC 5/05...
Replies
1
Views
1,521
Hello folks. I am just new to panelwview . I have to replace a bad panel view 1000 with a new one. I have the .mer file on my latop. While using...
Replies
5
Views
5,684
Hello; I'm programming a 1200 with RSLogix and a InView Panel 2706-P42R with Inview Messaging Software. I'm struggling with how to make the plc...
Replies
5
Views
4,174
I have a Panel View 550 kepad and touch running on DH-485 thru the RS-232 port. It losses communication with the netowrk at random. I have it...
Replies
7
Views
3,983
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
208
Back
Top Bottom