Can I download a configuration over Ethernet/IP to a Panelview Plus?
I also noticed in RSLogix that I did not add the Panelview to Controllogix logic.
Do you mean the I/O tree in RSLogix 5000 ?
Do not put a PanelView Plus in the I/O tree under an Ethernet module in RSLogix 5000.
That feature is for PanelView Standard terminals only.
Putting a "PanelView" object in the I/O tree as a child of an EtherNet/IP bridge module will result at best in a nuisance fault, and at worst in connection errors between the ControlLogix and the PanelView Plus.