PanelView Plus 7 (F/W 9) Trends Disappearing

phuz

Member
Join Date
Jun 2008
Location
Mohnton, PA
Posts
1,044
I have a customer with an issue on a relatively new PV+ 7 I put in, where the trend data disappears and I can't see anything until I re-download the app.
Can't find any rhyme or reason why this data just disappears.
Maximum points set for 1000000. 27 tags being collected every 10 seconds.
 
Last edited:
Are 27 tags being collected at the same time? Does the trend disappear right away or after certain time?
Is it running from internal memory? try external sd or upgrade to v10.
 
Are you definitely trending the same tags that are in the Data Log Model ?

Does the same effect occur when you test the runtime on a FactoryTalk View Studio development computer ?

I generally make a screen with a big FT Diagnostics viewer object so I can see any internal error messages that affect services like the Data Log Model right there on the PV+ terminal.
 

Similar Topics

Could use some help on setting a trend on a PV+1000. Is there a way to start and stop the trending based on a SLC500 Tag? I want to trend...
Replies
4
Views
2,913
I want to know if it is possible to plot a trend from values stored in an array. I have about 150 data points stored in an array in the PLC that...
Replies
3
Views
3,396
When i exit and open the trend screen trends disappear and restart again. Is there a way to keep the trend lines active when the screen is...
Replies
2
Views
6,412
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
99
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
64
Back
Top Bottom