PanelView Plus 7 - I need more then 200 alarms

JohanM

Member
Join Date
Sep 2015
Location
TerchovĆ”
Posts
53
Hi guys. I have another problem. This time with PanelView. I am working on project with PanelView Plus 7. It offers just upt to 200 alarms. But I need more then 200. Maybe 400 or more.šŸ™ƒ I can use also local messages, but that is not a best way. I need show more than 1 message (alarm) at once. Do you have some cheat for this kind of problem? :) Thank you very much!
 
Make sure FTView ME is not configured for the compact version. The compact version has a 200 alarm limit but your part number says you don't have one of those.
 
Oops, I was looking for the 'C' after the '2711P' like they did with the PV+ 6 versions. Sorry, didn't realize they switched the part numbering scheme. So a multi-state indicator may work or roll-your-own alarm system.
 

Similar Topics

Hi, guys, we have one production line with 5 Panelview Plus these are connecting to one Logix5000 via Ethernet. We want to change one...
Replies
1
Views
2,316
How do you assign a password on PanelView Plus? Ver.5.0 I've been trying allday and I'm worn out. Thanks
Replies
3
Views
5,167
I am trying to get a micrologix 1100 to communicate with my pv+ 400. I have quite a bit of experience with rs logix 500 but never have had to set...
Replies
7
Views
3,957
Hello friends, I am developing a application for Panelview plus 1000 colour using SLC 5/04 PLC. I have following with me : 1) SLC 5/04 PLC...
Replies
1
Views
13,771
i will be developing some screens for a customer for a PanelView 1000 Plus. my questions are: what version of RSView Studio, RSLinx...
Replies
19
Views
8,514
Back
Top Bottom