Inputs
Setpoint SP
Type a value between 1-16383, or within valid scaled range
The desired control point of the process variable. Enter this value via your ladder program to the third word in the control block (word 2).
Setpoint Max
(Smax)
Type in a value. (With 5/02 controllers the valid range is from -16383 to +16383. With the 5/03, 5/04, and 5/05 controllers the valid range is -32768 to +32767.)
If the setpoint is to read in engineering units, this corresponds to the value of the setpoint in engineering units hen the control input is 16383.
Setpoint Min (Smin)
Type in a value. (With the 5/02 controller the range is from -16383 to +16383. With the 5/03, 5/04, and 5/05 controllers the valid range is from -32768 to +32767.)
If the setpoint is to read in engineering units, then this parameter corresponds to the value of the setpoint in engineering units when the control input is zero.
Process Variable PV
(Read-only)
This is the scaled value of the Process Variable (the analog input). Without scaling, the range of this value is 0–16383. Otherwise, the range is minimum scaled (word 8) to maximum scaled (word 7).