PID_Compact S7-1200 strange error/warning
tim2
Nov 2004
245
Using TIA Portal V13 and PID_Compact to control a flow valve in a simple level control application using a pressure sensor.
The problem is somewhere in the output value limits/time configured for the cyclic interrupt OB.
If I configure the OB30 cyclic time for say a second or more, I get the following warning after a successful pretuning/fine tuning.
16#0020: The cycle time of the calling OB limits the sampling time of the PID algorithm. Improve results by using shorter OB cycle times.
Other than that, the pretuning and fine tuning work, PID parameters are calculated, and everything works.
If I configure it for shorter values, say 100ms, I get the following error during pretuning. (actually the progress bar goes really fast, when it reaches the end, it outputs the following error: (I can't find anything wrong with the output value limits, and it doesn't mind them with the longer cycle time)).
16#0080: Error during pretuning. Incorrect configuration of output value limits.
Everything still works afterward, but it faults out of the pretuning.
Help
Currently am trying to create a new project and copy components in one at a time until I find the part that's causing the problem.
Do you get an error if that register is not configured?
I think it will try to set its own cycle time if you leave it blank, also if tuning fails, it should go back to previous settings.
Dear All, I use PID Compact in PLC S7-1200 to control Motorized Valve (Danfoss) has Analong input 0-20mA this PID work for example for three, day...
1,906
I'm trying to use a PID_Compact Instruction in a S7-1200, but the Setpoint seems to be having no effect. Currently I'm using Totally Integrated...
6,316
I am totally new to this 1200 plc system, some one have simpel exampel how this block pid compact work. The sensor is a analog sensor that...
9,381
Hello all! First official post here... have been using the site for help but managed to find existing threads to help with all previous issues...
1,209
Hello. I am trying to figure out how to setup a PID in Control Logix 1769 Controller in a way that it would control a drive speed by sending...
1,627