Hello KHD2000;
On one hand you have a S7-300 PLC.
On the other, you have some sort of ELO touchscreen.
You would like to interface both.
Is this correct?
The S7-300 PLC does not generate by itself a video signal for a screen.
The old S5 platform had on some systems a video signal generator card for SCADA applications, but these were abandonned after the coming of age of the PC platforms.
If this touchscreen has an embedded computer that can run a HMI or SCADA package (Siemens' WinCC flexible, or WinCC, Citect, Wonderware, InTouch, IFix, and many others that have drivers or OPC connections for the S7-300 platform over Profibus, Ethernet or serial links), then you can buy and install them on the on board computer.
If the touchscreen does not have an embedded computer, you will need to connect it to a PC station (the screen expects a video input from a computer) and install the SCADA/HMI package of your choice on the PC, along with the communication driver or OPC server for the S7-300 platform.
Hope this helps,
Daniel Chartier