Hi All,

While Replacing a VFD in breakdown condition which is the right and easy way to replace the drive quickly. We are working with Plant PAX 3.5V/L-75 Processor/Studio 5000-32V. Please give brief idea to deal with breakdown condition.

Looking for quick reply
Thanks in Advance
 
The easiest method is to use ADC (Automatic Device Configuration) along with DHCP Persistence. This allows the PLC controller to store all the parameter information for the drive as well as the firmware.

When a replacement drive is installed, your Stratix Ethernet switch should be configured to use DHCP Persistence which would automatically assign the same IP address from the failed drive to the replacement drive.

Then once the IP address has been assigned, the ADC function would check the firmware of the replacement drive and if necessary upgrade/downgrade to the proper version. After that, the PLC controller would send all parameter information to the replacement drive. After that, the drive would be ready for use.

The PF753 doe not come with Ethernet built-in to it but it can be added through an option card. The drive has three slots available for option cards. This would require one of those slots. The PF525 has Ethernet built-in so it would not require any additional components.

OG
 
Then once the IP address has been assigned, the ADC function would check the firmware of the replacement drive and if necessary upgrade/downgrade to the proper version...
Just a small nitpick - the ADC doesn't do firmware. For that, you need firmware supervisor which is a completely different setting.

In my opinion, ADC without firmware supervisor is nearly useless, because I can almost promise that whatever drive you get off the shelf 5-10 years later to replace the failed one will have a different version of firmware. I never use one without the other.

To enable firmware supervisor, you need to set the compatibility setting for all the relevant drives to "exact match" (instead of "compatible module", which is the default). Then you need to load the firmware files onto the PLC's SD card by going to controller properties>non-volatile memory. You will have to switch the PLC to program mode while you do this. You must have the desired firmware files your your PC to be able to download them to the PLC's SD card, of course.

To give my answer to the OP's original question - I use ADC and firmware supervisor wherever possible. I have never yet set up an application with DHCP persistence because the only one of my clients that had that type of network structure, only had support for DHCP and not BOOTP. Powerflex 525 drives only support BOOTP unless you add the additional comms module.

My electrical drawings always contain a page (or pages) for parameter lists for all parameterisable devices, so when I'm using this strategy, my parameter list page for the VSD's consists of a short brief on what ADC/firmware supervisor is, and how to replace a failed drive - i.e. get the IP address/subnet mask/gateway from drawing ABC, enter them into parameters XYZ, and let the PLC do the rest.
 

Similar Topics

i have a flashing yellow sts light. "Stop Asserted" message on one of my PF 753"s, but no bits set in parameter 961. The safety circuit tests...
Replies
1
Views
208
Hi all I am working on a retrofit project. There is one backup pump with Powerflex 753 drive controlled by 2 different PLCs(one 1756-L63 ,one...
Replies
3
Views
1,536
Just wondering if anyone has run into a powerflex 753 has all the incoming power, but doesnt output any power to the motor, but doesnt display any...
Replies
5
Views
1,617
I'm looking at how to configure a (new to me) Power Flex 753 drive. The part number is as follows and has been specified by a third party...
Replies
6
Views
2,363
i have a problem in the drive 30 kw used with motor 4 pole (1770 rpm ) , and the motor used to run load with pulley ratio 2.3 so the load speed...
Replies
11
Views
4,902
Back
Top Bottom