Powerflex 4 field wiring question
Sep 2018
Chattanooga
68
So i’m Field engineering a panel for a 19’ conveyor we are building. The conveyor will have 3 - powerflex 4 drives. My question is concerning the start input on the drive. Can I feed the output off the PLC (+24v) straight to the drive for the start input? If so do I need to take my power supply common to terminal 4? Right now the only way to get it to work is have my PLC output fire a 24vdc coil and run my drive +24vdc through a set of NO contacts. But I want to do away with all the relays that are unecessary if possible.
Yup I do it all the time. Makes controlling drives much cleaner without relays all over the place.
Awesome. That’s one thing I’m trying to accomplish with this panel. Only the necessary components, as streamlined as possible. Thank you all for the replies.
The argument for interposing relays is that if anything goes wrong in your control wiring, it takes out a cheap relay that can be easily replaced, not the more expensive VFD. You can’t repair the control board on the VFD.
Yes, but it also makes troubleshooting twice as difficult and also adds a small amount of current for every relay you add. If all of your wiring for the VFD’s is integral to the cabinet then the chance of damage to the wiring itself is minimal. Also, a short on 24v system will reset the power supply. If I were running 120v controls then I would agree with you.
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
29
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
173
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
278
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
172
Hello everyone, I'm new here. First of all I just want to say that you guys are very knowledgeable and reading your posts on here has saved my...
176