problem in tansfer program to cpu 135u s5

amrhadad

Member
Join Date
Jun 2008
Location
cairo
Posts
17
after transfer program from PG to PLC (CPU 135 U STEP 5 )
STOP LED IS flashes
try to do manual cold restart
stop led still flashes
please help me (i wish know correct procedure to do manual cold restart after transfer program to my plc )
 
You don't say which type CPU you use, but here is the link to the manual for the 928B:
đź“š
http://support.automation.siemens.com/WW/view/en/19397726

The CPU is trying to tell you something. Look at page 4.3 - meaning of the LEDs:

Slow flashing;
The CPU is in the STOP mode.
The CPU itself prompted the STOP condition (possibly also of the other CPUs).
Typical causes:
ADF, QVZ, LZF, BCF, CL controller error, interrupt collision, cycle time error,
BSTACK overflow, stop command.
If you switch the mode selector to STOP, the flashing stops and the LED is lit
Quick flashing:
The CPU is in the STOP mode.
An overall reset has been requested. This request can be prompted by the CPU itself or
by an operator input.


Kalle
 
thank you
but i want know plc need to cold restart after transfer program to plc

1: Which CPU type do you use; 6ES592?-????????
2: Slow or fast stop LED flashing?
3: What kind of restart type is selected in DX0?
The STOP/RUN switch acts according to settings in DX0.
4: If I remember correctly you can select cold or warm restart from the Step5 software, the switch must be in RUN.
5: Did you reset the CPU before downloading?
6: Does the CPU start empty after reset?
7: What do you read in ISTAC + BSTAC?
:
Kalle
 

Similar Topics

Hello, I am a plc engineer and I have a job to do in the NIGERIA 25000 TON GRAIN SILOS STORAGE CONTROL PANEL. A problem where the panel is not...
Replies
1
Views
158
The project on the operator workstation keeps disconnecting, even though I have an installation server and operating station set up through...
Replies
0
Views
68
I have a problem, I'm running an AE Licence Manager on a Windows 2016 Server, and my Window Maker is on another separate Windows 2016 Server. My...
Replies
0
Views
107
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
Replies
1
Views
92
Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
Replies
23
Views
667
Back
Top Bottom