Garry,
You are correct, there currently is an issue with the Kadet units and the RLC instrument driver. Also as you stated we hope to have the fix included in our next release of the software.
I looked into the converter for you and the problem is actually with the literature for the G307K. In the port pinout for the Com3 RS232 the labeling for Tx and Rx are reversed. Regarding the Pin 5 comm connection, the reason you don't see it is because that connection doesn't cross connectors. There was not a need to connect common on all four connections because the ports on the units are not isolated.
Thanks
Jeremy
You are correct, there currently is an issue with the Kadet units and the RLC instrument driver. Also as you stated we hope to have the fix included in our next release of the software.
I looked into the converter for you and the problem is actually with the literature for the G307K. In the port pinout for the Com3 RS232 the labeling for Tx and Rx are reversed. Regarding the Pin 5 comm connection, the reason you don't see it is because that connection doesn't cross connectors. There was not a need to connect common on all four connections because the ports on the units are not isolated.