Prosoft MVI56E-MNETC w/ CLX

Pdell

Member
Join Date
May 2021
Location
Alaska
Posts
1
Controller: 1756-L84E v.35
Prosoft MVI56E-MNETC for ModbusTCP/IP

I'm having an issue with some of my write commands. The write command that I'm using individual bits within 1 word for an "enable", "start", "stop", etc will not work. If I'm writing lets say a setpoint for example 700DEGF it will write that value to the module

To see if it was a module problem, I used Mdbus to write to the specific control word and I'm able to "start", "stop", etc. so I know its a problem with the configuration in Studio5000 or Prosoft Configuration builder.

I also set the MNETC.CONTROL.CmdControl.WriteCmdBits to 1111_1111_1111_1111 to ensure all of the commands are enabled.

Enable YES
Internal Address 20
Poll Interval 0
Req Count 1
Swap Code No Change
IP Nunya
Serv Port 502
Slave Addr 1
*****Mdbus Func FC3 - Read Holding Registers *****
*****(I question this but it worked using Mdbus for troubleshooting)*****
MB Addres In Device 4311 (device end is 4312)

Diagnostics has NO errors.

I'm confident that what you might call "basic configuration" would be correct.

What could I be missing here?
 

Similar Topics

Hi all. I just received my brand new Prosoft Modbus modules and I'm playing with one in a L82 rack. I managed to set it up well enough so I...
Replies
4
Views
390
Hi All, I just wanted to confirm something regarding this module. What I understood from the manual, is that if RS-485 mode is selected (jumper...
Replies
2
Views
364
Hi all, I wonder what's the best type of cable to use for RS-485 2 wire + GND That is, Data+, Data- & GND I know that Belden 9841 (not...
Replies
10
Views
1,070
Does anyone have and is able to share a firmware file for the ProSoft MVI56E-MNET module (Modbus module for a Rockwell PLC)? I have an...
Replies
0
Views
1,333
Does anybody have experience using a Prosoft MVI56E-MCM module and a ebmpabst W3G910-KV12-61 (or similar) fan motor? The Modbus register list...
Replies
4
Views
1,610
Back
Top Bottom