PV1000 with multiple SLC500's ???

JerryH

Member
Join Date
Mar 2009
Location
Tellico Plains,TN
Posts
110
I have a short line with 3 AB PLC504's connected with DH+ and would like to connect a Panelview 1000 to them. Is the Panelview capable of connecting and communicating with the 3 plcs at the same time over DH+? or do I need one for each plc?

Jerry
 
Last edited:
Short answer is yes, but first you need to tell us which of your statements is correct. Are they SLC 5/03's or are they DH+? 5/03s use DH485 and 5/04s use DH+.
 