Good afternoon,
Last week I had an issue with noise affecting some Kinetix 6500. A new analog drive was installed about 5 feet below these drives, but the gains on the drive were not set properly. This caused interference on the A.B. Kinetix drives and caused them to fault out. Lowering the gains on the analog drives solved the problem.
I wanted to hear other examples from people here in this community on their own noise-related issues, how they troubleshooted, etc. This noise issue seems very difficult to pinpoint and I would like to here other people's stories on how they prevent noise from causing too much problems in their panels.
Hopefully these examples will help me improve my own troubleshooting and design skills in the future.
Thanks (y) ,
Check for proper grounding. Avoid wires that are too long, or coiled up excessively. Run signal wires separately from power wires. Ask the manufacturer, in your case Allen Bradley since they make the Kinetix 6500, for suggestions on how to reduce noise.
Any drives, servo, vfd, whatever, I put line reactors on their power inputs. When I'm commissioning a panel that doesn't have them and exhibits similar problems to what you're describing I start with installing line reactors. And in each case problem disappeared.
We commissioned a Kinetix 6500 driving an old Anorad linear motor. All was well until we coupled the motor to its load at which point we started getting feedback faults. We ended up running the shielded motor cable through a separate grounded conduit and experimented with different grounding methods (ground at the motor, at the drive, both, etc.) until we found scheme that worked. No noise issues in a couple of years of operation.
Hello everyone, I am looking to get a job as a junior automation engineer. I know the basics of PLC programming with Rockwell and Siemens PLCs...
1,783
Good Morning Everyone, I am entry level PLC programmer and this is going to be my first PLC project at my company. I would like to thank you for...
4,233
Hi all, [Long message alert!] I’m after some advice on training courses. I’d like to know what the general consensus is regarding the PLC...
3,674
Dear all, I took a PLC course in college. The course was mainly doing basic relay type programming. I did not need to worry about setting up the...
2,686
Hey everyone, I think i'm in a little over my head. school made me very confident with the familiarity of Rockwells software; RSLogix5000...
5,251